You should not have any trouble with six wired in series as most alarm systems have a generous zone for violated and non-violated indications.
Some things to watch. Make sure they are truly in "series". The best way to test is with a meter on the wire ends that go into the security panel. Remove the wires from the panel and measure them with the meter in "ohms" range. With all contacts closed the reading will probably be somewhere between 2 and 12 ohms (without using EOL, with EOL the reading will be within its range). Then open and close one contact at a time and see if the reading goes to infinity.
Also, if you are using EOL type of zones, make sure you install only ONE resistor in the ENTIRE series loop (probably best located at the contacts furthest from the panel).
Thanks for the info. I'll make sure to follow your advice on testing. This is my first system I've installed, and I'm pretty sure I'm going with the ELKM1G. That being said are all systems normally closed? I couldn't find the info for ELK and I'm looking at these window contacts
http://www.smarthome.com/7352.html because of their size. The info on the contacts states "Contacts are closed when magnet and sensor are together" so I'm confused if they're NO or NC. But the real question is, can I use them with the ELKM1G?
Thanks again,
Rich