View attachment 3684I think you are on the right track. I was confused by your drawing but it still may be correct. I have attached a drawing to show you what I am saying. Just remeber that you may have to play around with the relay as far as NO and NC goes.
Hope this helps
MERRY CHRISTMAS
Hi, I'm a new member here learning and trying to understand the many ideas as I prepare for my own M1G installation.
This is in reference to the diagram posted by ahellard on 12/23/10.
In lieu of the separate relay and aux power supply, would it be possible to use the ELK-P212S (Supervised Remote Power Supply) in M1 mode as follows:
RRS-MOD Red <---> P212S 12V+ (pos)
RRS-MOD Black <---> P212S 12V- (neg)
RRS-MOD Orange <---> P212S 12V- (neg)
RRS-MOD Yellow <---> P212S Output B NC
P212S 12V+ <---> P212S Output B COM
Then write a rule to the effect of:
Whenever smoke reset
Then turn output xxx (the Output B on the P212S) ON for a few seconds.
This ought to energize the Output B relay, momentarily cutting power to the smokes to unlatch and reset them.
However, if an alarm condition exists and the smokes are annunciating (Output 3 from the M1G ON) that means the RRS-MOD is taking [reversed] power to the smokes via the Red+/Black- pair rather than the Yellow+/Orange- pair (see the RRS-MOD schematic). That means momentarily cutting power just to Yellow+ while in alarm condition will have no effect on resetting the smokes.
Thus, would it be appropriate to wire RRS-MOD Red <---> P212S Output B NC as well, rather than to an always-on 12V+?
Finally, is it necessary to run a separate negative from the P212S back to the MG1? Or will the Black (neg) on the RS485 data bus take care of that?
Thanks!