Elk M1 & ELKRP2, Outputs > 64

Yes. M1XOVR address 12 shows up in the enrolled list as Type 3 but the ElkRP2 outputs only show up to 64.
 
I checked with Elk support on this, to use outputs 65 and up you need to program them via keypad and refer to them in rules by specifying the output number. Outputs over 64 cannot be named in ElkRP2.
 