Here is this mornings log from NextAlarm of one of my customers.
Oct 07, 2006 04:14:47 AM External Siren 2 Restored
Oct 07, 2006 04:07:20 AM External Siren 2 Failure
Oct 07, 2006 04:07:17 AM External Siren 2 Restored
Oct 07, 2006 04:05:06 AM External Siren 2 Failure
Oct 07, 2006 04:05:01 AM Interior Violation Master Bedroom Motion - (Zone 5)
Oct 07, 2006 04:04:58 AM Perimeter Violation Front Door - (Zone 1)
Oct 07, 2006 04:04:44 AM Interior Violation Master Bedroom Motion - (Zone 5)
The External Siren 2 Failures were caused by an overcurrent condition based on running two ELK-45's not on MilliMiserâ„¢ setting. I would like to avoid having to rewire the sirens if at all possible. I would appreciate anyone who has powered two ELK-45's from the M1 without overcurrenting and without rewiring the sirens to respond. To those who are using two ELK 150-RT's beware, it tests fine but after it runs for a few minutes it overcurrents. It is so annoying that in testing I generally don't let the siren wail for more than a minute so it never overcurrented in testing.
My biggest concern is the reporting to the CS the front door violation when in fact there was none. If you look at the log it looks like someone got in the master and went out the front door. Based on that it looked like it might have been a real alarm. However, the front door never violated and was dead bolted. There was a previous thread about this adjacent zone false violation reporting condition but I could not find it. I would like to revive that thread here and determine if anything is being done about it. I am using 4.4.2 firmware, one step down from the latest. TIA
Oct 07, 2006 04:14:47 AM External Siren 2 Restored
Oct 07, 2006 04:07:20 AM External Siren 2 Failure
Oct 07, 2006 04:07:17 AM External Siren 2 Restored
Oct 07, 2006 04:05:06 AM External Siren 2 Failure
Oct 07, 2006 04:05:01 AM Interior Violation Master Bedroom Motion - (Zone 5)
Oct 07, 2006 04:04:58 AM Perimeter Violation Front Door - (Zone 1)
Oct 07, 2006 04:04:44 AM Interior Violation Master Bedroom Motion - (Zone 5)
The External Siren 2 Failures were caused by an overcurrent condition based on running two ELK-45's not on MilliMiserâ„¢ setting. I would like to avoid having to rewire the sirens if at all possible. I would appreciate anyone who has powered two ELK-45's from the M1 without overcurrenting and without rewiring the sirens to respond. To those who are using two ELK 150-RT's beware, it tests fine but after it runs for a few minutes it overcurrents. It is so annoying that in testing I generally don't let the siren wail for more than a minute so it never overcurrented in testing.
My biggest concern is the reporting to the CS the front door violation when in fact there was none. If you look at the log it looks like someone got in the master and went out the front door. Based on that it looked like it might have been a real alarm. However, the front door never violated and was dead bolted. There was a previous thread about this adjacent zone false violation reporting condition but I could not find it. I would like to revive that thread here and determine if anything is being done about it. I am using 4.4.2 firmware, one step down from the latest. TIA