Operating BOTH INSTEON and X-10 devices: (Special attention to Jumper S5)
It is possible for the M1XSP to communicate with both INSTEON and traditional X-10 devices. It works as follows: Upon
activation of a Lighting device the M1XSP (with special INSTEON Firmware) will send INSTEON commands for the lighting
devices number that have an INSTEON linked address. It will send X-10 commands for the lighting devices that do not have
an INSTEON "linked" address. This helps to eliminate the need for a separate X-10 PSC05 or TW523 Interface. However,
there are tradeoffs and limitations which must be accepted. For example: No X-10 devices can have a House/Unit code that
conflicts with any present or future linked INSTEON device locations. Lighting devices are numbered 1 (A01) to 256 (P16).
See the chart on the next page. INSTEON device linking BEGINS at Lighting device 1 (A01) and ENDS at 192 (L16). For this
reason, do not assign X-10 House/Unit codes in the extreme low numbers. Furthermore, no X-10 House/Unit codes can be
assigned to light device addresses 193 (M1) through 256 (P16), as these are reserved for INSTEON Groups and special
commands. There is an option to eliminate Groups and free up addresses 193 (M1) to 254 (P14). See note N2 below.