kgingerich
Member
I installed my ELK-WSV and ran 18 awg 4 conductor wire to the M1G panel. I wired up the red, black, and white wires per the instructions that came with the WSV to the relay OUT 3 on the panel.
I wrote an automation rule to turn on OUT 3 whenever any of my water sensor zones become not ready. I wrote the rule so that OUT 3 would stay on for 5 minutes so I can test that it works.
I tested the rule and can hear a click in the panel and OUT 3 LED light turns on but the water valve doesn't close. I used a multimeter to test for 12VDC on OUT3 and get nothing on either the N/C or N/O leads.
Any ideas?
Kyle
I wrote an automation rule to turn on OUT 3 whenever any of my water sensor zones become not ready. I wrote the rule so that OUT 3 would stay on for 5 minutes so I can test that it works.
I tested the rule and can hear a click in the panel and OUT 3 LED light turns on but the water valve doesn't close. I used a multimeter to test for 12VDC on OUT3 and get nothing on either the N/C or N/O leads.
Any ideas?
Kyle