HAI temp / Humd Sensor Issues

scottp73

Member
I just installed the Extended range TEMP/HUMD Sensor and am having an issus with what it is reporting. I am getting an temp of 72 outside when it is only 50 out. And the Humd is reporting 92 - 108 % What could be causing this to be so OFF?


Thanks for your help in advance!
 
Did you designate it as a "Temperature" zone or "ER Temperature" zone?
Use the "ER Outdoor Temperature" zone for the outdoor sensor, only one allowed on a system.
Others must be "ER Temperature".

If you use the "Temperature" zone type the temps will be off with an ER sensor.

Ask me how I know...
 
Did you designate it as a "Temperature" zone or "ER Temperature" zone?
Use the "ER Outdoor Temperature" zone for the outdoor sensor, only one allowed on a system.
Others must be "ER Temperature".

If you use the "Temperature" zone type the temps will be off with an ER sensor.

Ask me how I know...

Always happy to oblige - How do you know?
 
Thanks so much!!! that was the Problem!! The Humidity is off on it's reading but I can work with what it is sending me!! Once again thank you!!!
 