I would also double check your calculated loading on the P624 as it seems low.[*] 1.65 amps typical through the M1G (average battery backup time = 48 hours) powering
[*] 0.45 typical through the P624 (average battery backup time = 17.5 hours) powering
Here's how I calculated the typical on the P624:
- 4 M1XSP @ 0.03 amp typical == 0.12 amp
- 1 M1XRF2G @ 0.07 amp typical == 0.07 amp
- 4 M1KP2 @ 0.03 amp typical == 0.12 amp
- 3 M1KPAS @ 0.03 amp typical == 0.09 amp
- 2 M1DBH @ 0.00 amp typical == 0.00 amp
- 5 ASD200 @ 0.01 amp typical == 0.05 amp
giving typical 0.45 amp total. Alarm status adds 0.06 amp to each keypad, 0.01 amp to each arming station, and 0.07 amp to each smoke detector, giving alarm total as 1.06 amp. The WSV (1.0 amp), the fireplace (0.38 amp) are short-term only.
Am I missing something?
If your backlights are all of the way down then you are correct. I have mine at about 8 or so and the KP version so they are closer to 80 ma or more each. I though you were more like 650 ma plus.