What did you use as the temperature sensor?
Are you measuring the temperature of the floor or the air in the room?
Thanks,
I know this sounds like a great idea, but here's the problem... Most floor heat thermostats perform a calculation to estimate the heat capacity of the floor. With a regular thermostat, it would turn on the heat and continually heat the floor until the room temperature reaches the set point, and then shut off. The floor will be hotter than the room temp, and the temp of the room will continue to skyrocket past the set point. Then it must drop to below the set point, and the cycle starts over.
With thermostats made for floor heat, they will monitor how quickly the room heats up and cools down, and then make a calculation that will turn on the pump every 15-20 minutes for a period of time calculated to keep the temp in the room stable. For example, my garage heat in the winter turns on every 20 minutes for about 2-3 minutes.
What you need is a communicating thermostat that can talk to the HAI that calculates the heat capacity of the floor, and as far as I know, no one makes one. However, Aube does make one that you can remotely control to day/night mode. My day setting is 65F, and my night setting is 50F. It's just two terminals that are on the back of the unit, and when you bridge them it puts it in night mode. So it's a start, but it doesn't give you full control. For $45 though, it's not a bad deal, and if you're replacing a thermostat that doesn't do the calculations, you'll probably save this in energy costs the first month you run it if you're in a cold northern climate.