Any help would be appreciated as I am completely stumped. I am trying to connect two RC1000 HAI thermostats to an EWC NCM300 zone panel. I have connected the Zone 1 thermostat and it works fine. The Zone 2 thermostat also appears fine but when it calls for cool or fan the HCAC system is not activated. I have confirmed that there is 24VAC at the R and C at the thermostat. Thus it doesn't appear to be a power issue at the thermostat. I have also confirmed hat if i short G to R at the thermostat the fan goes on. Thus it doesn't appear to be a wiring problem or problem with the zone panel. I also confirmed that although a call is indicated (and there is a click too) there is not 24VAC between the Y/G and C terminals at the panel. Lastly, i have changed the Z1 and 2 thermostats and they both work fine while on Z1 so it would seem it isn't the thermostat either. So, it seems that for some reason the thermostat is not passing the voltage to the terminals (Y or G) when there is a call. Any ideas? Any help would be greatly appreciated!