Hi,
Building new home. HVAC guy checked and said RC-2000s would work.
HVAC guy connected RC-2000s to a WaterFurnace Zone controller and Zone controller "thought" that the RC-2000s were calling for heat/cool even when the RC-2000s were not.
HVAC guy spoke to someone at HAI (I am told) and was informed that he needed to add external relays between the RC-2000s and the Zone control for 3 of the RC-2000 outputs (I wish I wrote down which ones). Something to do with certain outputs of the RC-2000 passing a small amount of current even when "off" and fooling the Zone controller.
Anyone heard of this sort of problem?
Thanks!
Building new home. HVAC guy checked and said RC-2000s would work.
HVAC guy connected RC-2000s to a WaterFurnace Zone controller and Zone controller "thought" that the RC-2000s were calling for heat/cool even when the RC-2000s were not.
HVAC guy spoke to someone at HAI (I am told) and was informed that he needed to add external relays between the RC-2000s and the Zone control for 3 of the RC-2000 outputs (I wish I wrote down which ones). Something to do with certain outputs of the RC-2000 passing a small amount of current even when "off" and fooling the Zone controller.