Here are the voltage readings in the Not Ready state- it doesn't trigger using the above wiring :DELInstallations said:Have you metered voltage between the A and - with the sensor in both normal and alarm states?
Is the power common with the panel?
Is the zone conductor landed on the HIGH and not COM of the panel?
No other EOLR is installed on the single zone conductor (only a single one should be landed at the panel besides the power pair).
9.83 between + and A
3.75 between - and A
re 'is the power common with the panel' - the + is from a +12v aux on the panel and the - is to aux ground on the panel.
I don't understand what you mean by the zone conductor being on HIGH not COM.
There is no other EOLR on that zone