[M1ZTS Stability] . . . There are many circumstances where it will bounce between 2 temperatures (ie, 74/75) for several minutes before stabilizing. . .
I have not noticed this either. Bobble has not been an issue.
I think Spanky's post was speaking to the possibility that JayH's setup was being incorrectly monitored - - Unless I got it wrong...
Anyhow -
I have 2 external Elk sensors and they are always close to what I think they should be.. No bobble here either.
I wish I had the stability you guys seem to have. I'm aware of the calibrations and have set them in the past - not in the last couple years. As far as firmware, I keep pretty close because of some of the new messages that have been added in the last 8-12 months.
My outside ZTS is mounted up in the corner of eves on the southeast side and is showing 37 degrees. My Fluke 87 is sitting about 2' away on the window sill with the sensor probe stretched and sitting within about 3" of the ZTS - it is showing 31.  Is this possibly just an issue with radiated heat from the house being picked up by the ZTS?
On the bobbling, this has nothing to do with rules - I've been converting the messages into events and logging them for a long time. The device here is the outside temperature sensor for 8/20/2009 from midnight to midnight reporting the ST messages from the elk. Sorry for the length, but I figured if I cut anything there would be questions. I don't know what the real high (or low) was for the day but you can see the "bobble" in the ST messages and the time marks.  It's not a firmware issue - I have 2 years of this logged across 3 firmware versions that I'm aware of.
00:35:08 R/1 1:028 value NewValue 87 OldValue 88
00:35:24 R/1 1:028 value NewValue 88 OldValue 87
00:35:40 R/1 1:028 value NewValue 87 OldValue 88
00:35:56 R/1 1:028 value NewValue 88 OldValue 87
00:36:28 R/1 1:028 value NewValue 87 OldValue 88
00:37:00 R/1 1:028 value NewValue 88 OldValue 87
00:39:08 R/1 1:028 value NewValue 87 OldValue 88
00:39:24 R/1 1:028 value NewValue 88 OldValue 87
00:40:12 R/1 1:028 value NewValue 87 OldValue 88
00:41:16 R/1 1:028 value NewValue 88 OldValue 87
00:41:48 R/1 1:028 value NewValue 87 OldValue 88
00:42:52 R/1 1:028 value NewValue 88 OldValue 87
00:43:08 R/1 1:028 value NewValue 87 OldValue 88
01:48:30 R/1 1:028 value NewValue 86 OldValue 87
01:48:46 R/1 1:028 value NewValue 87 OldValue 86
01:49:50 R/1 1:028 value NewValue 86 OldValue 87
01:51:10 R/1 1:028 value NewValue 87 OldValue 86
01:52:14 R/1 1:028 value NewValue 86 OldValue 87
01:52:46 R/1 1:028 value NewValue 87 OldValue 86
01:53:34 R/1 1:028 value NewValue 86 OldValue 87
01:53:50 R/1 1:028 value NewValue 87 OldValue 86
01:54:22 R/1 1:028 value NewValue 86 OldValue 87
01:55:10 R/1 1:028 value NewValue 87 OldValue 86
01:55:42 R/1 1:028 value NewValue 86 OldValue 87
01:57:18 R/1 1:028 value NewValue 87 OldValue 86
01:58:22 R/1 1:028 value NewValue 86 OldValue 87
01:59:58 R/1 1:028 value NewValue 87 OldValue 86
02:00:30 R/1 1:028 value NewValue 86 OldValue 87
02:02:38 R/1 1:028 value NewValue 87 OldValue 86
02:03:10 R/1 1:028 value NewValue 86 OldValue 87
02:03:58 R/1 1:028 value NewValue 87 OldValue 86
02:04:14 R/1 1:028 value NewValue 86 OldValue 87
02:07:59 R/1 1:028 value NewValue 87 OldValue 86
02:08:15 R/1 1:028 value NewValue 86 OldValue 87
02:10:55 R/1 1:028 value NewValue 87 OldValue 86
02:11:11 R/1 1:028 value NewValue 86 OldValue 87
03:28:33 R/1 1:028 value NewValue 85 OldValue 86
03:29:05 R/1 1:028 value NewValue 86 OldValue 85
03:32:01 R/1 1:028 value NewValue 85 OldValue 86
03:32:33 R/1 1:028 value NewValue 86 OldValue 85
03:33:21 R/1 1:028 value NewValue 85 OldValue 86
03:33:37 R/1 1:028 value NewValue 86 OldValue 85
03:34:57 R/1 1:028 value NewValue 85 OldValue 86
03:35:13 R/1 1:028 value NewValue 86 OldValue 85
03:35:29 R/1 1:028 value NewValue 85 OldValue 86
03:36:01 R/1 1:028 value NewValue 86 OldValue 85
03:36:17 R/1 1:028 value NewValue 85 OldValue 86
03:36:33 R/1 1:028 value NewValue 86 OldValue 85
03:37:21 R/1 1:028 value NewValue 85 OldValue 86
03:37:53 R/1 1:028 value NewValue 86 OldValue 85
03:38:09 R/1 1:028 value NewValue 85 OldValue 86
03:41:37 R/1 1:028 value NewValue 86 OldValue 85
03:41:53 R/1 1:028 value NewValue 85 OldValue 86
03:49:21 R/1 1:028 value NewValue 86 OldValue 85
03:49:37 R/1 1:028 value NewValue 85 OldValue 86
03:53:05 R/1 1:028 value NewValue 86 OldValue 85
03:53:21 R/1 1:028 value NewValue 85 OldValue 86
05:07:16 R/1 1:028 value NewValue 84 OldValue 85
05:07:32 R/1 1:028 value NewValue 85 OldValue 84
05:08:20 R/1 1:028 value NewValue 84 OldValue 85
05:08:52 R/1 1:028 value NewValue 85 OldValue 84
05:10:12 R/1 1:028 value NewValue 84 OldValue 85
05:10:28 R/1 1:028 value NewValue 85 OldValue 84
05:12:20 R/1 1:028 value NewValue 84 OldValue 85
05:13:24 R/1 1:028 value NewValue 85 OldValue 84
05:15:32 R/1 1:028 value NewValue 84 OldValue 85
05:16:20 R/1 1:028 value NewValue 85 OldValue 84
05:17:24 R/1 1:028 value NewValue 84 OldValue 85
05:17:40 R/1 1:028 value NewValue 85 OldValue 84
05:18:12 R/1 1:028 value NewValue 84 OldValue 85
05:19:48 R/1 1:028 value NewValue 85 OldValue 84
05:20:04 R/1 1:028 value NewValue 84 OldValue 85
09:41:31 R/1 1:028 value NewValue 85 OldValue 84
09:42:03 R/1 1:028 value NewValue 84 OldValue 85
09:42:35 R/1 1:028 value NewValue 85 OldValue 84
09:54:52 R/1 1:028 value NewValue 86 OldValue 85
10:10:52 R/1 1:028 value NewValue 87 OldValue 86
10:11:24 R/1 1:028 value NewValue 86 OldValue 87
10:11:56 R/1 1:028 value NewValue 87 OldValue 86
10:24:44 R/1 1:028 value NewValue 88 OldValue 87
10:30:21 R/1 1:028 value NewValue 89 OldValue 88
10:38:53 R/1 1:028 value NewValue 90 OldValue 89
10:49:17 R/1 1:028 value NewValue 91 OldValue 90
10:54:21 R/1 1:028 value NewValue 92 OldValue 91
11:03:58 R/1 1:028 value NewValue 93 OldValue 92
11:13:34 R/1 1:028 value NewValue 94 OldValue 93
11:26:06 R/1 1:028 value NewValue 95 OldValue 94
11:35:26 R/1 1:028 value NewValue 96 OldValue 95
11:37:18 R/1 1:028 value NewValue 95 OldValue 96
11:37:35 R/1 1:028 value NewValue 96 OldValue 95
11:41:19 R/1 1:028 value NewValue 97 OldValue 96
11:44:47 R/1 1:028 value NewValue 98 OldValue 97
11:51:27 R/1 1:028 value NewValue 99 OldValue 98
11:56:47 R/1 1:028 value NewValue 100 OldValue 99
12:03:11 R/1 1:028 value NewValue 101 OldValue 100
12:03:43 R/1 1:028 value NewValue 100 OldValue 101
12:03:59 R/1 1:028 value NewValue 101 OldValue 100
12:09:19 R/1 1:028 value NewValue 100 OldValue 101
12:12:15 R/1 1:028 value NewValue 101 OldValue 100
12:12:31 R/1 1:028 value NewValue 100 OldValue 101
12:21:36 R/1 1:028 value NewValue 99 OldValue 100
12:21:52 R/1 1:028 value NewValue 100 OldValue 99
12:22:08 R/1 1:028 value NewValue 99 OldValue 100
12:22:24 R/1 1:028 value NewValue 100 OldValue 99
12:22:40 R/1 1:028 value NewValue 99 OldValue 100
12:22:56 R/1 1:028 value NewValue 100 OldValue 99
12:23:28 R/1 1:028 value NewValue 99 OldValue 100
12:23:44 R/1 1:028 value NewValue 100 OldValue 99
12:24:16 R/1 1:028 value NewValue 99 OldValue 100
12:31:44 R/1 1:028 value NewValue 98 OldValue 99
12:32:00 R/1 1:028 value NewValue 99 OldValue 98
12:32:16 R/1 1:028 value NewValue 98 OldValue 99
12:48:00 R/1 1:028 value NewValue 99 OldValue 98
13:21:05 R/1 1:028 value NewValue 100 OldValue 99
13:23:13 R/1 1:028 value NewValue 99 OldValue 100
13:25:22 R/1 1:028 value NewValue 100 OldValue 99
13:25:54 R/1 1:028 value NewValue 99 OldValue 100
13:26:26 R/1 1:028 value NewValue 100 OldValue 99
13:26:42 R/1 1:028 value NewValue 99 OldValue 100
13:26:58 R/1 1:028 value NewValue 100 OldValue 99
13:39:30 R/1 1:028 value NewValue 99 OldValue 100
13:40:34 R/1 1:028 value NewValue 100 OldValue 99
13:57:54 R/1 1:028 value NewValue 99 OldValue 100
13:59:14 R/1 1:028 value NewValue 100 OldValue 99
14:02:27 R/1 1:028 value NewValue 99 OldValue 100
14:02:43 R/1 1:028 value NewValue 100 OldValue 99
14:13:07 R/1 1:028 value NewValue 99 OldValue 100
14:13:39 R/1 1:028 value NewValue 100 OldValue 99
14:14:43 R/1 1:028 value NewValue 99 OldValue 100
14:14:59 R/1 1:028 value NewValue 100 OldValue 99
14:15:31 R/1 1:028 value NewValue 99 OldValue 100
14:15:47 R/1 1:028 value NewValue 100 OldValue 99
14:16:19 R/1 1:028 value NewValue 99 OldValue 100
14:16:35 R/1 1:028 value NewValue 100 OldValue 99
14:16:51 R/1 1:028 value NewValue 99 OldValue 100
14:30:27 R/1 1:028 value NewValue 98 OldValue 99
14:30:43 R/1 1:028 value NewValue 99 OldValue 98
14:32:51 R/1 1:028 value NewValue 98 OldValue 99
14:47:32 R/1 1:028 value NewValue 97 OldValue 98
14:47:48 R/1 1:028 value NewValue 98 OldValue 97
14:48:36 R/1 1:028 value NewValue 97 OldValue 98
14:49:24 R/1 1:028 value NewValue 98 OldValue 97
14:50:28 R/1 1:028 value NewValue 97 OldValue 98
14:51:48 R/1 1:028 value NewValue 98 OldValue 97
14:52:04 R/1 1:028 value NewValue 97 OldValue 98
15:05:56 R/1 1:028 value NewValue 98 OldValue 97
15:07:16 R/1 1:028 value NewValue 97 OldValue 98
15:07:32 R/1 1:028 value NewValue 98 OldValue 97
15:30:13 R/1 1:028 value NewValue 97 OldValue 98
16:29:59 R/1 1:028 value NewValue 96 OldValue 97
16:30:15 R/1 1:028 value NewValue 97 OldValue 96
16:30:47 R/1 1:028 value NewValue 96 OldValue 97
17:04:40 R/1 1:028 value NewValue 95 OldValue 96
17:04:56 R/1 1:028 value NewValue 96 OldValue 95
17:05:12 R/1 1:028 value NewValue 95 OldValue 96
17:05:28 R/1 1:028 value NewValue 96 OldValue 95
17:06:16 R/1 1:028 value NewValue 95 OldValue 96
17:06:48 R/1 1:028 value NewValue 96 OldValue 95
17:07:04 R/1 1:028 value NewValue 95 OldValue 96
17:07:20 R/1 1:028 value NewValue 96 OldValue 95
17:07:36 R/1 1:028 value NewValue 95 OldValue 96
17:07:52 R/1 1:028 value NewValue 96 OldValue 95
17:08:08 R/1 1:028 value NewValue 95 OldValue 96
17:08:56 R/1 1:028 value NewValue 96 OldValue 95
17:09:12 R/1 1:028 value NewValue 95 OldValue 96
17:09:28 R/1 1:028 value NewValue 96 OldValue 95
17:09:44 R/1 1:028 value NewValue 95 OldValue 96
17:38:33 R/1 1:028 value NewValue 94 OldValue 95
17:38:49 R/1 1:028 value NewValue 95 OldValue 94
17:40:57 R/1 1:028 value NewValue 94 OldValue 95
17:41:13 R/1 1:028 value NewValue 95 OldValue 94
17:41:29 R/1 1:028 value NewValue 94 OldValue 95
17:42:01 R/1 1:028 value NewValue 95 OldValue 94
17:43:05 R/1 1:028 value NewValue 94 OldValue 95
18:36:58 R/1 1:028 value NewValue 93 OldValue 94
19:29:16 R/1 1:028 value NewValue 92 OldValue 93
19:29:32 R/1 1:028 value NewValue 93 OldValue 92
19:30:20 R/1 1:028 value NewValue 92 OldValue 93
19:30:36 R/1 1:028 value NewValue 93 OldValue 92
19:31:08 R/1 1:028 value NewValue 92 OldValue 93
19:31:24 R/1 1:028 value NewValue 93 OldValue 92
19:32:12 R/1 1:028 value NewValue 92 OldValue 93
19:33:00 R/1 1:028 value NewValue 93 OldValue 92
19:33:16 R/1 1:028 value NewValue 92 OldValue 93
19:58:21 R/1 1:028 value NewValue 91 OldValue 92
19:58:37 R/1 1:028 value NewValue 92 OldValue 91
20:00:13 R/1 1:028 value NewValue 91 OldValue 92
20:01:33 R/1 1:028 value NewValue 92 OldValue 91
20:01:49 R/1 1:028 value NewValue 91 OldValue 92
20:27:57 R/1 1:028 value NewValue 90 OldValue 91
20:28:29 R/1 1:028 value NewValue 91 OldValue 90
20:29:49 R/1 1:028 value NewValue 90 OldValue 91
20:30:21 R/1 1:028 value NewValue 91 OldValue 90
20:30:53 R/1 1:028 value NewValue 90 OldValue 91
20:31:58 R/1 1:028 value NewValue 91 OldValue 90
20:32:14 R/1 1:028 value NewValue 90 OldValue 91
20:32:30 R/1 1:028 value NewValue 91 OldValue 90
20:33:02 R/1 1:028 value NewValue 90 OldValue 91
21:03:26 R/1 1:028 value NewValue 89 OldValue 90
21:05:18 R/1 1:028 value NewValue 90 OldValue 89
21:05:34 R/1 1:028 value NewValue 89 OldValue 90
21:34:23 R/1 1:028 value NewValue 94 OldValue 89
21:34:39 R/1 1:028 value NewValue 89 OldValue 94
21:38:39 R/1 1:028 value NewValue 88 OldValue 89
21:38:55 R/1 1:028 value NewValue 89 OldValue 88
21:40:47 R/1 1:028 value NewValue 88 OldValue 89
21:41:03 R/1 1:028 value NewValue 89 OldValue 88
21:42:07 R/1 1:028 value NewValue 88 OldValue 89
21:42:39 R/1 1:028 value NewValue 89 OldValue 88
21:42:55 R/1 1:028 value NewValue 88 OldValue 89
22:25:05 R/1 1:028 value NewValue 87 OldValue 88
22:25:21 R/1 1:028 value NewValue 88 OldValue 87
22:26:09 R/1 1:028 value NewValue 87 OldValue 88
22:26:41 R/1 1:028 value NewValue 88 OldValue 87
22:29:05 R/1 1:028 value NewValue 87 OldValue 88
22:29:21 R/1 1:028 value NewValue 88 OldValue 87
22:31:45 R/1 1:028 value NewValue 87 OldValue 88
22:32:01 R/1 1:028 value NewValue 88 OldValue 87
22:32:49 R/1 1:028 value NewValue 87 OldValue 88
22:33:05 R/1 1:028 value NewValue 88 OldValue 87
22:34:41 R/1 1:028 value NewValue 87 OldValue 88
22:35:13 R/1 1:028 value NewValue 88 OldValue 87
22:35:45 R/1 1:028 value NewValue 87 OldValue 88
Don't get me wrong - I really like the Elk M1 and am doing a lot with it - but temperature is one of the sore spots for me based on my experiences. Show me how to fix it.
Jay