For reading:
http://www.elkproducts.com/support/tech-note_965.html
I am unable to locate the Altronix note since they redesigned their site.
You need to be very careful with generators and alarm equipment, especially residential grade hardware. Electronics do not like frequency variations and noise on the AC lines.....causes a LOT of issues. I deal
weekly with multiple sites that have massive generators that are tested weekly that have very sophisticated equipment for monitoring and controlling them...VFD's and the like. There are constant issues with FACP's and access panels that are on UPS/standby power after the gen tests. Consider the size and complexity of these generators that are supplying power to critical equipment (lifesaving and other) compared to a small residential unit.
I'm at a loss, if you don't have any draw out in the field, then why the need for such a large supply and battery? It doesn't make sense. If your draw is that small and you direct buried, you might as well just run everything off the supply and installed it within the house and eliminate that design issue (unless there is a large distance and significant voltage loss).
You need to be realistic with your standby time on the panel M1. How long are you intending on the unit to last without commercial power? Have you done the calcs? In the case of the 212S, you were given a maximum battery size by Elk, you can't exceed that number so you're going to need to derate the standby time for the lowest temperature the supply is going to see while maintaining the 20% safety cushion. Now you have that number, so that's going to need to be a higher standby time than your M1 standby time otherwise you're going to have trouble....When the M1 loses expanders with devices on them, especially security, or they're rebooting as the remote system is at it's threshold for the devices running (M1, about 12V is when things start getting funky) then you're not going to like the event log and the notifications, especially if the system is monitored.
I have about 10 pages of CS traffic from a single system where the tech note came from, with remote devices and power supply that I missed the derating factor and chose a unit that lost voltage upon conversion...then had battery sag, the LBC switch issue AND devices rebooting and going offline causing phantom alarms and system traffic. Not a pretty site (and shame on me for not noticing the fine specs of the supply and missing the derating to have the supply last less time than the panel).
After doing the calcs and comparing it to the M1, if it doesn't meet your standby time spec without commercial power, then you have a design issue and the 212S is the wrong unit for your application.
As far as derating factors, almost every battery manufacturer provides tables on their product, but usually it is a very significant factor, even up to 30-40% of listed rating.