Ok so I am still eating up batteries in my new thermostat....


soooooo what i need is a hvac guru.... or.....someone with the same setup as me..

who here has a

gas heater and central air conditioning..
their wire running from the hvac to the thermostat only has 4 wires....

and they have the wayne dalton or ca8900 thermostat....


here is what i posted elsewhere on another forum...

Ok so I took a thermostat out..
honeywell... it had 4 wires that go back to my hvac unit..

Red
Green
White
Blue

Thermostat
Red went to R
Green went to G
White went to W
Blue went to Y ( I looked and it is Y on both ends.. 4 conductor wire so they used the blue...)

anyway..
my new thermostat is
intermatic z-wave ca8900

they want me to hookup
Red to R
Green to G
White to W
then they throw a +C to C

well I have the hvac unit hooked up the way my old system was and it works... everything works.. but the C is 24vac to keep the thermostat running.... so instead it is eating up batteries...

what do I do?
just run a new wire back and connect C to the controller board of C????

on the controller board there is everything I listed above with an additional...

C - white wire
then a red wire from that pair goes to Y

so how do I get 24vac to the thermostat???


if you go here
http://www.hometech.com/learn/hvac.html

and goto the section labeled
24VAC Heat/Cool Non-Heat Pump

that is the wires I have now... but need to figure out how to get 24vac to the thermostat so I wont run off of batteries....

I ran a jumper from r to c figuring that if red is voltage it should supply a jump to C... but that didnt work... still killed the batteries in a few days....

anyone know???
thanks
Jeff
 
Your red wire is connected to one side of the 24VAC transformer in your system. Connecting the "C" terminal to that line ain't gonna work -- you haven't closed the loop. The "C" terminal MUST be connected to the OTHER side of the transformer secondary coil in order to provide a return path for the current. The "C" designation is for Common -- that other side typically represents the common for the system. If you only have 4 wires, you'll need to add another line from the transformer in your system to the C terminal on your CA8900. Make sure you understand which wires are coming out of that transformer -- and don't confuse the primary with the secondary, unless you like pyrotechnics. Use a multimeter to double check.
 
Your red wire is connected to one side of the 24VAC transformer in your system. Connecting the "C" terminal to that line ain't gonna work -- you haven't closed the loop. The "C" terminal MUST be connected to the OTHER side of the transformer secondary coil in order to provide a return path for the current. The "C" designation is for Common -- that other side typically represents the common for the system. If you only have 4 wires, you'll need to add another line from the transformer in your system to the C terminal on your CA8900. Make sure you understand which wires are coming out of that transformer -- and don't confuse the primary with the secondary, unless you like pyrotechnics. Use a multimeter to double check.


thanks... yeah got it working... had to run a 5 wire back to the heater... once I did that... connect to C on both ends and viola... no more eating up batteries.... ;)
 
thanks... yeah got it working... had to run a 5 wire back to the heater... once I did that... connect to C on both ends and viola... no more eating up batteries.... ;)

I had the same issues - using Intermatics CA8900; Batteries were running out almost daily. I connected Blue wire (common) to C on the thermostat but then I had to go back on the furnace, connect the Blue/Common wire to 'C' on the furnace curcuit board and it then Worked for me too...Thanks for the raising this question. It helped today...
 