Ok so I am still eating up batteries in my new thermostat....
soooooo what i need is a hvac guru.... or.....someone with the same setup as me..
who here has a
gas heater and central air conditioning..
their wire running from the hvac to the thermostat only has 4 wires....
and they have the wayne dalton or ca8900 thermostat....
here is what i posted elsewhere on another forum...
Ok so I took a thermostat out..
honeywell... it had 4 wires that go back to my hvac unit..
Red
Green
White
Blue
Thermostat
Red went to R
Green went to G
White went to W
Blue went to Y ( I looked and it is Y on both ends.. 4 conductor wire so they used the blue...)
anyway..
my new thermostat is
intermatic z-wave ca8900
they want me to hookup
Red to R
Green to G
White to W
then they throw a +C to C
well I have the hvac unit hooked up the way my old system was and it works... everything works.. but the C is 24vac to keep the thermostat running.... so instead it is eating up batteries...
what do I do?
just run a new wire back and connect C to the controller board of C????
on the controller board there is everything I listed above with an additional...
C - white wire
then a red wire from that pair goes to Y
so how do I get 24vac to the thermostat???
if you go here
http://www.hometech.com/learn/hvac.html
and goto the section labeled
24VAC Heat/Cool Non-Heat Pump
that is the wires I have now... but need to figure out how to get 24vac to the thermostat so I wont run off of batteries....
I ran a jumper from r to c figuring that if red is voltage it should supply a jump to C... but that didnt work... still killed the batteries in a few days....
anyone know???
thanks
Jeff
soooooo what i need is a hvac guru.... or.....someone with the same setup as me..
who here has a
gas heater and central air conditioning..
their wire running from the hvac to the thermostat only has 4 wires....
and they have the wayne dalton or ca8900 thermostat....
here is what i posted elsewhere on another forum...
Ok so I took a thermostat out..
honeywell... it had 4 wires that go back to my hvac unit..
Red
Green
White
Blue
Thermostat
Red went to R
Green went to G
White went to W
Blue went to Y ( I looked and it is Y on both ends.. 4 conductor wire so they used the blue...)
anyway..
my new thermostat is
intermatic z-wave ca8900
they want me to hookup
Red to R
Green to G
White to W
then they throw a +C to C
well I have the hvac unit hooked up the way my old system was and it works... everything works.. but the C is 24vac to keep the thermostat running.... so instead it is eating up batteries...
what do I do?
just run a new wire back and connect C to the controller board of C????
on the controller board there is everything I listed above with an additional...
C - white wire
then a red wire from that pair goes to Y
so how do I get 24vac to the thermostat???
if you go here
http://www.hometech.com/learn/hvac.html
and goto the section labeled
24VAC Heat/Cool Non-Heat Pump
that is the wires I have now... but need to figure out how to get 24vac to the thermostat so I wont run off of batteries....
I ran a jumper from r to c figuring that if red is voltage it should supply a jump to C... but that didnt work... still killed the batteries in a few days....
anyone know???
thanks
Jeff