my assumption was that the black on switch #1 (in the drywall) was going to the load, but the entry I bolded is backwards, therefore my assumption must be wrong. And in my assumptions, changing switch #1's position wouldn't change any voltages at switch#21st switch:2nd switch:
- black -> white : ON=118V OFF=0V
- black -> red : ON=0V OFF=0V
- black -> ground : ON=0V OFF=118V
- white -> black : ON=118V OFF=0V
- white -> red : ON=118V OFF=0V
- white -> ground : ON=118V OFF=118V
- red -> white : ON=118V OFF=0V
- red -> ground : ON=0V OFF=0V
- red -> black : ON=0V OFF=0V
- black -> white : ON=0V OFF=118V
- black -> red : ON=0V OFF=118V
- black -> ground : ON=118V OFF=118V
- white -> black : ON=0V OFF=0V
- white -> red : ON=0V OFF=118V
- white -> ground : ON=118V OFF=118V
- red -> white : ON=0V OFF=118V
- red -> ground : ON=0V OFF=0V
- red -> black : ON=0V OFF=118V
switch#2 black is always hot, so I am still sure that is the feed
I suggest opening the wirenut with the two black wires (circuit break off if you are safe) and try to verify if that is the load by seeing of the light no longer works and measuring the voltage of the loose wires.
And you should only need to get voltage with respect to ground, the voltage between the various colors doesn't really add any details since this is all 100V on/off stuff.