WayneW
Nope, the current is the same in the whole wire path.When installing these CT's...does it matter if they're close to the termination lugs or breakers?
With the spil CT's you don't have to disconnect the main feed from the main breaker (main breaker and panel itself should ofcourse be off) and for the micro CT's you just unterminate from the breaker, slip on the CT and put it back in...all of course with the main breaker OFF.
I just don't know if I should use electrical tape of similar to fix the CT's in a certain position on the conductors or not.
I supposed the variour leads from the CT's can all come together and exit the panel though a knockout with strain relief and go to the unit right?
Are the CT's shipping with these units UL listed now? I thought this was an issue some time ago.
If they're not UL listed i would think you'd have a hard time getting a sparky to put them in.
BtechRep,
The specially-priced CocoonTech package, equipped with the older model, was a popular promotional offer. Will Brultech be running a similar promotion with the new model?
Or is the new offer mentioned somewhere in these 17 pages and I just can't find it ...
(2) Is this unit capable of dealing with a 240Y (open delta) residential feed? We discussed this back in September but the 1220 wasn't capable of handling this. I realize I can't get a perfect reading because of 2-transformer setup and single voltage reference, is there a way to use 1, 2 or 3 CT's in a series configuration with the appropriate resistors & multiplier to get close? (5 Ton A/C unit for those interested)
Jay
Jay
In the 3-phase configuration of which the "open delta" is a specific case, the mains voltages are shifted by 120 degrees wit respect to each other. Therefore, it is impossible to calculate power using only one voltage channel as is done with the split phase configuration where you can pretend that each leg has the same voltage and just sum up current transformer outputs. If you attempted the same with the open delta, your power reading would be about 25% lower for resistive loads.
Jay
Clarification please...
Impossible in a 3-phase configuration (ie, A/C unit) or impossible in my 120/240V panel that services the rest of the house because the phase-phase in that panel is 120 instead of 180? If you are talking about the 120/240V panel then wouldn't I have a high neutral current because it is completely unbalanced? (I don't)
In the case of the A/C unit - it would be an independent channel and I'm looking for a "close" measurement - be it 1 ct * sqrt(3) or other factor, or 3 summed with a multiplier.
Thank you for the guidance.
Jay
Jay
Jay
Jay,
My understanding is that your house gets a three wire (two phases and the neutral) open delta feed. The AC unit is connected to two phases. The rest of the house is more or less distributed between the two phases. Is that correct ?
If so, your panel voltage is probably 120/208 (sqrt(3)*120) volts rather than 120/240 and the AC unit gets 208 volts. In the open delta systems, the neutral current is rather high due to grossly unbalanced phases. For example if you have perfectly balanced 50Amp resistive loads on two phases, the neutral current would also be 50 Amp. However, you said that it is not the case. There are several possible explanations:
o You did not measure the neutral current correctly (unlikely). Did you measure the current directly on the mains neutral wire where it enters your house ?
o You have a separate 120/240 ordinary residential feed in addition to the open delta feed for your AC.
o You have a real three-phase feed, your AC has a three phase motor, the house loads are distributed between three phases and your imbalance is not substantial.
We can take this offline since this isn't directly related, unless others are interested and have a similar (odd) configuration.
A Picture that Paul found that represents the voltages/legs correctly is below. My feed from the pole is 3 phases (A/B/C) and Neutral. HOWEVER the picture is showing a single transformer but the pole is using a 2-transformer setup with #1 feeding the A/C legs 120/240/neutral and #2 feeding B which is 240 to A, 240 to C and 208 to neutral. I am running the air conditioning compressor using all 3 legs 240 leg/leg - no neutral.
"3 phase 4W Delta-connected. This illustration shows a three-phase, four wire, delta-connected secondary. There are 240 volts from phase to phase. The midpoint of one phase winding is grounded to provide 120V A/N and 120V C/N. Between B/N, however, the voltages is 208V. This is referred to as the high leg."
So, I have to ask, does anyone have an ethernet version of the 1240 running with any software? So far, it sounds like the people that are writing interfaces to the 1240 are depending on COM port. However, from the documentation, I don't believe there is a COM port when you use the Etherbee or Etherport? So, if you go the network route, is there or will there be any software that will work with it?
Jesse