I am planning for install of M1G.
I was looking to get System Sensor 4WTB smokes/thermal and 5601 thermal detectors. I am homerunning each back to panel on separate zones. I already ran 22/4 wire (I realize now i should have installed larger gauge...) but runs are max of 30feet to panel so SSensor said this should be fine.
House already contains 120volt smokes in rooms/spaces, tied together, with siren. This system required by code, will NOT be tied to alarm system. Since i wanted a monitored system, with information as to what zone is going off, i am installing one or two detectors per floor.
SSensor recommended installing the EOLR-1 for each smoke. From reading some posts, it seems like with the M1G, it is not necessary, all you need is the end of line resistor.
Is this correct?
Thanks.