OK. So we all agree now. Let me summarize.
1. Within a circuit, it is OK to tie neutrals from various loads (on that circuit) together.
2. It is not OK to tie neutrals from different circuits together (except for the multiwire branch circuit). Neutrals for different circuits come together only at the breaker panel.
3. The multiwire branch circuit is where two circuits of equal capacity and on opposite phases may share a neutral. In this case, the neutral is not overloaded because it carries only the inbalance of the two circuits, ie. the difference in the two circuit currents instead of the addition of the two circuit currents if they were in-phase.
4. As already mentioned in the thread, although the code allows sharing a neutral for a multiwire branch circuit, is not good practice because of safety concerns.
1. Within a circuit, it is OK to tie neutrals from various loads (on that circuit) together.
2. It is not OK to tie neutrals from different circuits together (except for the multiwire branch circuit). Neutrals for different circuits come together only at the breaker panel.
3. The multiwire branch circuit is where two circuits of equal capacity and on opposite phases may share a neutral. In this case, the neutral is not overloaded because it carries only the inbalance of the two circuits, ie. the difference in the two circuit currents instead of the addition of the two circuit currents if they were in-phase.
4. As already mentioned in the thread, although the code allows sharing a neutral for a multiwire branch circuit, is not good practice because of safety concerns.