Maybe try doing a factory reset on the bathroom switches and try again. I used that when mine were acting wierd and it helped a bit (same ones I am returning though as my particular issue returned).
I ran tests on my detectors. Here is what I did.
1. I triggered the suspect detector (the last one in the loop) using a canned spray tester. It went into an alarm condition and was triggered.
2. I went to the keypad and entered a user code, the panel stopped.
3. I then went to elk function 2 and reset the detectors, it worked fine and the detector reset (no reversing relay in place right now so only that one detector fired).
4. Granted I had to reset it a few times as it would go off and then 15-20 seconds later or so it would trigger again (remnants of the canned tester I am assuming). I used a compressed air can to clear the area and it stayed reset and did not activate again after that.
As such, I am assuming my inability to reset the detectors originally was because I was using the installer code (which isn't allowed to).
I am also thinking back to the first false alarm, I am fairly certain I looked in each room and there was no red light on any of the detectors. Not positive, but close as that should have been prominent and I did look at each one (not really thinking about the red light at the time though). I'm assuming even if they were all connected with the RRS-MOD/2W-MOD2, I still should have seen a red light on the triggered alarm (that should not have affected the basic functionality of the detector).
My 30 second alarm cutoff also worked, the first time it went off I waited for it to reset and it did work properly. The detector continued to trigger.
My assumption then is that I have an intermittent wiring issue on the last leg between the fourth and fifth detector, possibly enhanced by having the RRS-MOD and 2W-MOD2 (just a guess).
If the detector was getting stuck, I should not have been able to reset it right? Also I understand this should not have happened on a new detector either.
Is there any way to further test the wire (would any tests show the issue?)? I am going to replace that leg with a new run of wire and change the zone to fire verified. In addition I am going to hook it up to the phone (hadn't done that since I was planning on internet monitoring) and have it call me and my wife if it goes off. Then I can dial in to reset it (and have my wife or a neighbor check it if we are not home). Listen in would be cool as well, but I think the above should help for now.
If any of the assumptions above seem flawed, please let me know as well. From the feedback I've gotten it seems to explain my issues.
Thank you for all the help on this.