I have 5 Costar 12-25SIR gas sensors. Apparently they haven't been working integrated with the Omnipro, just individually.
I can't get them to work properly with Omnipro.
This is what I have:
Gas Sensors are wired daisy chained in a Normally Open configuration.
They are connected to Omnipro Zone 3. I have zone jumper set to SMK. Zone type is set to GAS.
Gas zone shows trouble all the time.
If I wire them in a normally closed configuration and change jumper to normal, set zone type to Auxiliary the zone will show secure.
What am I doing wrong that it won't work as a gas zone setup?