Senior Member
Starting to wire it up, have another question. Do you then program OUT3 to activate when zone 16 is violated? Also, SAUX is switched so SDs could be reset. How do I switch it, could it be programmed into one of the F keys on the keypad. Is "11=Fire Verified" used for that?
thank you
1) Not exactly. You have output 3 active on fire alarm. This will cover any fire situation that you might add to the alarm in the future that isn't zone 16.
2) Power cycling the smokes is done through the keypad menu. No need to asign it a function key (not sure you even can, never tried it)